IEC 61850 .cid file import
Hi to all. I have dilemma about how some files are imported with .cid file. Example: When I open xyz.cid file in notepad++ a get 6 values of mag.f[MX] type, but when I do import and when I filter those same tags with same name, there are more tags with
Reading COMTRADE files automatically
Hi, I need to read COMTRADE files from a bunch of relays (35-40) in a substation. The operator has requested a function by which all COMTRADE files can be read automatically (either by a single button or at a fixed time). Does anyone have some idea on
Command Information IEC61850
Hi all, Could I ask how to add command information (Select, Operate, Cancel) into Zenon 7.5 ? I followed the step of manual (Additional Cause Diagnosis) to create 2 variables *Oper.ControlRun and *Oper.ControlState according to the varible *Oper.ctVal[CO]
Interlocking teks
Hello I created an Interlock for additional controlbutton in commandprocessing display. For every Interlock you can set the Interlocking tekst. I expected to see the interlock text in the same Interlocking tekst indication in the Commandprocessing dialog.
IEC680, Qualifier of command, Befehlsgabe
Hello! I have a Problem with the Interlocking check. It Looks like that this flag is not set. In the helping Information i can read that this function only works with "Auto/Remotebefehl" and "Pulsbefehl" and not with "Schaltbefehl". Is this correct? thanks!
Workspace file cached locally?
Hi, I have experienced quite a strange issue while working with the Zenon editor across different machines, with the editor losing changes when editing on a different machine to the previous time. Maybe you can advise what may be the cause.... Some basic
Extraction of Files through IEC 101
hi, i am using Zenon energy edition 7.5, Problem 1: case 1: i have a IED of IEC 61850 and its connected to a gateway (SEL-2241) which give IEC 101 to Zenon, now that IED has a Disturbance recorder (COMTRADE) files in it and i need to extract those through
Zenon Energy, Switch status shown in Alarm list after spontaneous open or close event
Hello, I would be pleased if you let me know how I can show the status of one switch(like circuit breaker in substation) after any spontaneous changes happened to that switch as we can see in SLD, but I could not see any record in ALM or CEl in runtime!
Delay in reaction matrix
Hi to all I have such problem. I have binary variable with rema with 2 states: 0 - normal, 1 - error. All states write in CEL. Error state have delay of 5 seconds to hide short errors. So if variable will be in error state less than 5 seconds then there
Power Curve
Hi Guys I am working related to Wind Industry. I want to draw Power Curve and Scatter Plots in Zenon. I couldn't find a way to do that. Anyone who has implemented, please help me regarding this. This is a migrated post! Originally posted on 24.07.2017
Modbus Driver not switching between adapters
Hi Support team I'm using Zenon Energy 7.5 and communicating with IEDs using Zenon 61850 Driver through redundant fiber switches (L2 & L1) Also I'm monitoring the switches alarms and port status using Modbus Driver in Zenon. My Srvr (windows 7 Pro) has
Scaling Problem
Hi, I have Volt and Amp data from different IEDs via Modbus TCP and IEC 61850. My problem is: - I need Amp (current) scaling factor to be adjustable by user input in runtime. There should be some code which will pop-up input screen on pressing "Settings"
Gis
Hi Guys I am working related to wind industries. Have some doubts in Editing GIS. 1.How to insert text in GIS (Eg. Name of the Wind Turbine near to the marker) 2.How to insert a variable value in the GIS (Eg. Power and Wind speed of that turbine near
COMTRADE and Motor Start Trending
Hello Support, For Zenon 7.5, the feature of reading COMTRADE file to show the waveforms is there, my question is : for motor start trending which motor protection relay has it, can we show it in zenon using COMTRADE file? Thank you in advance Best regrds.
IEC61850, import variables from driver
When using the "Import variables from driver" for IEC61850 protocol in zenone 7.5 - variables are not downloaded in full. We have access only to the variables available for display (read area) only . Access to a variable with the ability to send control
IEC61850: connection lost but varaibles non updated
Hi, i have a big problem in zenon, in particular in IEC61850 client driver. Driver has 20 connections to different RTUs. Problem appears when I turn off RTU. I will aspect that driver has INVALID status for each variables of that RTU, instead Zenon reads
IEC61850: connection lost but varaibles non updated
Hi, i have a big problem in zenon, in particular in IEC61850 client driver. Driver has 20 connections to different RTUs. Problem appears when I turn off RTU. I will aspect that driver has INVALID status for each variables of that RTU, instead Zenon reads
Command Processing
Hello! I have Double point (DP) commands which I need to switch via command processing. it's obvious how to do it But I've got a problem how to open different command screens for different command direction. I mean: 1 case) I want to switch ON, then I
Zenon 7.11 is incompatible with Multiltin ( 61850 ) Protection Devices
We are currently using Zenon V7.11 as our HMI / SCADA. We cannot get it to successfully get data from GE Multilin G60 and F650 Protection Devices using 61850. The issue is that the Zenon needs to set an integrity period when initialising the 61850 MMS
Hierarchical control interlocking
Hi Could you give me a suggestion about Process Gateway? I have 02 dispatching centre connected to the system via IE101 process gateway and I want to make a hierarchical control interlock between its. I have 03 button control 03 internal variables (HMI,
IEC60870-103 Unable to read analog measures
Hi, i have a big problem. I want to read three analog measures from a protection using iec870-103 protocol via serial communication. Zenon has a IEC870-103 driver correctly configured: it can read variables states from protection. My problem come when
Zenon 7.2 with new build
Hello support, For one of our project, zenon 7.20 is using with DNP3 master to integrate with GE RTU and read data ( digital inputs outputs and analog inputs), we had issue of reading correct analog data from GE RTU, and our engineer sent you about this
Screen Types missing
Hi, when i look path "C:\Program Files (x86)\COPA-DATA\zenon 7.20 SP0\Templates\ScreenTypes\ENGLISH" i can see 33 different Screen Types. When i start Zenon 7.20 editor and going to Screens->new screen-> select "Screen Type" now i can see only about 20
Load Management in Zenon Supervisor
Hi, Can anyone help me with the configuration of "Load Management" into a zenon design ? I would like to know how it works and how should I assign variables into the design ? Please help me with that, your help is appreciated. Thank you. !! This is a
Filter T_STD Event/Alarmlist
Is it possible to filter messages with the status T_STD out of the event/Alarmlist We see these messages comming whenever the communication to an IED is restored. And the timestamp is from the time that var has changed (e.g. local/remote). So that can
IEC104 Double Command Issue
Hi, I'm using Zenon 7.20 to communicate with SYS600 9.3 (ABB) Gateway through IEC104. When I do Process Command (T46): Select then Confirm ---> Close or Open Ok! Select then Cancel = Select then Confirm. Select then Exit = Select then Confirm. The Command
SCD Import to Zenon
Hi, I imported an SCD file from an ABB IED to zenon and managed to import variables. I created proper functions based on some of those variables and assigned them to buttons and so on. However, I couldn't operate a switch with the buttons and also I couldn't
Need help with Sicam 230
Dear Gents, Could you please explain: I have Sicam 230 SCADA and at present moment it's in operations. For example i need to change something in the active project (signals, signs etc.). When all changes are done do i need to restart the runtime on servers?
REG-DA (IEC 61850) in Zenon 7
i want to use an icd file of REG-DA in 61850 protocol in zenon HMI Would you please send me your setting of 61850 Driver configuration if you were succeed to read the status of AVR relay I cant read the status i can import Online & Offline but the value
Comtrade/ disturbance File Automatic extract
Hi.. 1. I am trying to configure the Automatic disturbance file extracting/uploading to station HMI the system has be configured such that it should extract the disturbance records from any relay ( any manufacturer) which support IEC 61850 file transfer.
61850 SCL or ICD import
Hi, I have a rather simple question. I want ti import SCL or ICD files from 61850 IEDs to Zenon. I know there is a way to do it but do not know how. If someone could tell me how the procedure is done, I would much appreciate it. Thanks This is a migrated
Operator Warnings
Hi, I'm programming at the moment a Sicam 230 System and I have a question concerning the recommended way to program Operator Warnings: At the moment, for my 220kV Circuit Breakers, I have created an object in the Symbol Library. This object contains
KEMA certification for IEC60870-10X
Dear all, I am interested in knowing if the stack of Straton for IEC60870-10X is Kema certifie? Please let me know if the protocol stack has this certification. Thanks Jos© Loreto. This is a migrated post! Originally posted on 24.11.2015 by user jloreto.
Zenon ENERGY Edition and Runtime
Hai Friends, I hope everybody doing well. I have one Power System Automation Project and using Zenon 7.20 energy edition editor and runtime license. Please find below my list quires, I need your support and suggestion to resolve the issues and satisfy
IEC 60870-5-103 command & response
Hi, How to create a command with a variable is double indication and double command. In IEC103, value OFF, ON is 1, 2, not 0, 1 and I can not active write set values. I have created a command but could not. I using the SIEMENS 7SJ62 relay. Thanks, Lang
IEC 60870-5-103 private ASDU
Hi, Can private range ASDUs (32-255) be received by Zenon? For example ASDU 77 from Schneider Electric Micom relays? This is a migrated post! Originally posted on 20.08.2015 by user okhotnikov. Please be aware that information can be outdated.
IEC 61850 variables not recognized in AML
Dear Copadata Team, I'm working with Zenon 7.11 SP0 Build 12493 64Bit. Unfortunately the IEC 61850 variables are not recognized/displayed by the alarm message list (or the chronological event list). However they are displayed in the "alarm frame" and
IEC61850 - Problem recieving goose
Hi! I am running a SCADA system on two computers on the same network. They are recieving goose messages from a raspberry pi running straton. However, 1 of them does no recieve the goose message even though the ZENON SCADA Workspace is identical. Do you
Trend Issue - Cannot reach the archived data
Hello guys, As a newbie on zenOn, I've been facing with a problem on making a trend screen. I've prepared the template and configured the historian but when I try to create a trend for a previous (or recent) month or week, it draws a trend line only for
Sicam 7.00 Build3 Runtime unexpectedly going to shutdown
Hello, Runtime is going to freeze after 20-30 min. later it's going to shutdown without giving any error when I simulate single point or double point signals from RTU or Field. Before going to shutdown, i can see all changes in this signals at AK Driver.