Interlockings
Hello, I have a problem with the interlockings module. It looks like in case that one of the variables is INVALID, The interlock will not work. Also what is strange is that the INVALID statusbit is not shown in the uncollapsed list of the statusbit, but
NET_SEL Variable
Good Morning, I am making a HMI for a test environment. And this is HMI includes an option to control switching objects. I have made a dynamic element (Switching object) that flashes when i have it selected. (NET_SEL is HIGH). When i execute the command
Comtrade Files Transfer to Client Machine
Hi, I have an issue while reading Comtrade files from the client machine in particular even though everything is exactly matching between machines and the internal variables of comtrade function in Zenon 7.11 are in network mode, I am able to retrieve
Hardware Requirements
Hi support, We want change an exisiting SCADA to Zenon EE, but client wants use the existing computers (hot stand by system). The computers are: - Model: UNO4683 Manufacter: Advantech W7 PRO Core i7 2.0 GHz 4G DDR3 SDRAM 64GB SSD - Model: ECU4784 Manufacter:
PloGGIO Block - IEC 61850 with Alstom Micom P443/P444
Hi everyone, I must send command with 61850 to Alstom Micom p443. I want to use PloGGIO block for that. However I can not find when i am importing to editor. I can see and control that block with IED Scout. Also try importing from .cid file, I can see
[SIPROTEC 5 7SJ82] Issue with command processing... even with command qualifier
Gabriel Simon [email]gabriel.simon@engie.com[/email] PS: I'm suing ZenOn EE 7.60 SP0 with Windows 10 Pro Server 64 bits mode PPS: I can send you a backup of the project if you want.[/FONT] This is a migrated post! Originally posted on 07.02.2018 by user
Polling Analog values each 1 second using DNP3.0 Protocol
Hi, We need pool Active Power and Frequency from a SEL-735 meter (Schweitzer) using DNP3.0 or other protocol with time stamp. Our client ask us to save data each 1 second (no by deadband). Could be possible with ZEE using DNP3 or another protocol (IEC61850,
"fpm.cmp" error
Hi I have a computer has install Zenon 7.50 runtime. Last time I use Zenon Editor 7.50 to config system, now I use Zenon 7.6 to config and compile/create runtime for 7.50 But I have a error :" If I change to create runtime for default (7.6) . I do not
Integration of Alstom relays
Hi Support, Its possible integrate Alstom relays (like BM9100 or KMPC130) using K-BUS or another Alstom protocol?. Thanks in advance for your support. Regards, Jos© Luis Torres This is a migrated post! Originally posted on 18.04.2018 by user jose.torres@indexum.com.
Coloring like lines
Hi, I am using Zenon Energy Edition 7.60. I want to color any shape exactly like Line with using ALC. There is option to check "color from ALC "box for Line Properties , altough being same option for other shapes I can't use it. What should I do for coloring
World view frame
Hi, Is it possible to open a worldview screen with 0% zoom? I have a screen for world navigation with a size of 4400/2550. When it opens, it opens already with a 100%%zoom. Is it possible to changed that? This is a migrated post! Originally posted on
Message in unhandle exception
Hi I have a problem log /2/2018, 10:16:06 AM zenOn Version: 7.60 SP0 Build36068 Processor: UNKNOWN //----------------------------------------------------- Exception code: C0000409 The system detected an overrun of a stack-based buffer in this application.
Error while runtime creation about variables which doesn't exists in database. Help is required to solve this error
Dear Team, Error while runtime creation about variables which doesn't exists in database. Help is required to solve this error. This is a migrated post! Originally posted on 04.05.2018 by user saravanan1985. Please be aware that information can be o
Reg: DPC Testing with varibale daignosis
Hi Team, Thanks to all your support in forum. I have a iec850 device which has double point. How can i test in varibale diagnosis. Simply adding variables will work or Do I have to create anything to test. Regards Sarav This is a migrated post! Originally
ALC Function Type (Switch,Disconnector)
Dear, I am SCADA engineer who is new in zenon using v7.60 . I have a question related to Automatic Line Coloring (ALC) Function Types switch and disconnector. When I choose Switch or Disconnector as a function type for a combined element, coloring is
EXCEL REPORT SAMPLE-Version 7.60 required
Hello guys, I require an Excel report sample for Zenon- 7.60 version at the earliest. Hope you guys can help with. This is a migrated post! Originally posted on 13.06.2018 by user saravanan1985. Please be aware that information can be outdated.
Invert read from IED
Hi guys I got a variable that is read from an IED using IEC61850, with a symbolic address to one of the GGIOs. As I need the signal inverted, I'm using the screen Status Definition to invert the visualization. However, I need to send this signal inverted
Inrush Current Not captured in trend
Hello Support, I am facing one issue that, motor starting current (Inrush current) is not captured by online/archive trend. Please support on this. Communication over modbus tcp. Used zenon-7.20 Win7 professional This is a migrated post! Originally posted
Befehlsgabe Doppelsignal IEC104
Hallo, ich habe hier ein zenon Projekt vor mir. Dabei gibt es sporadisch Fehler bei Schaltbefehlen. Nun habe ich versucht das Verhalten mit einer SPS nach zustellen, allerdings bekomme ich keine Schalthandlung zustande. Wenn ich die entsprechenden Zustände
CEL Not filling
Hello, I am trying to get a CEL to work on my HMI. When i start and stop the system it gives an message in my CEL and also when i switch an object an event is shown. when i use another variable and link it to a reaction matrix no entry in the CEL is shown.
Send control when unack alarm is raised
Afternoon, I was wondering what the best method would be for activating a control output when there are unacknowledged alarms standing in the system. In my case I would like to activate an external alarm (eg a Klaxon) by sending a control to my RTU (via
IEC 61850 .cid file import
Hi to all. I have dilemma about how some files are imported with .cid file. Example: When I open xyz.cid file in notepad++ a get 6 values of mag.f[MX] type, but when I do import and when I filter those same tags with same name, there are more tags with
Reading COMTRADE files automatically
Hi, I need to read COMTRADE files from a bunch of relays (35-40) in a substation. The operator has requested a function by which all COMTRADE files can be read automatically (either by a single button or at a fixed time). Does anyone have some idea on
Command Information IEC61850
Hi all, Could I ask how to add command information (Select, Operate, Cancel) into Zenon 7.5 ? I followed the step of manual (Additional Cause Diagnosis) to create 2 variables *Oper.ControlRun and *Oper.ControlState according to the varible *Oper.ctVal[CO]
Interlocking teks
Hello I created an Interlock for additional controlbutton in commandprocessing display. For every Interlock you can set the Interlocking tekst. I expected to see the interlock text in the same Interlocking tekst indication in the Commandprocessing dialog.
IEC680, Qualifier of command, Befehlsgabe
Hello! I have a Problem with the Interlocking check. It Looks like that this flag is not set. In the helping Information i can read that this function only works with "Auto/Remotebefehl" and "Pulsbefehl" and not with "Schaltbefehl". Is this correct? thanks!
Workspace file cached locally?
Hi, I have experienced quite a strange issue while working with the Zenon editor across different machines, with the editor losing changes when editing on a different machine to the previous time. Maybe you can advise what may be the cause.... Some basic
Extraction of Files through IEC 101
hi, i am using Zenon energy edition 7.5, Problem 1: case 1: i have a IED of IEC 61850 and its connected to a gateway (SEL-2241) which give IEC 101 to Zenon, now that IED has a Disturbance recorder (COMTRADE) files in it and i need to extract those through
Zenon Energy, Switch status shown in Alarm list after spontaneous open or close event
Hello, I would be pleased if you let me know how I can show the status of one switch(like circuit breaker in substation) after any spontaneous changes happened to that switch as we can see in SLD, but I could not see any record in ALM or CEl in runtime!
Delay in reaction matrix
Hi to all I have such problem. I have binary variable with rema with 2 states: 0 - normal, 1 - error. All states write in CEL. Error state have delay of 5 seconds to hide short errors. So if variable will be in error state less than 5 seconds then there
Power Curve
Hi Guys I am working related to Wind Industry. I want to draw Power Curve and Scatter Plots in Zenon. I couldn't find a way to do that. Anyone who has implemented, please help me regarding this. This is a migrated post! Originally posted on 24.07.2017
Modbus Driver not switching between adapters
Hi Support team I'm using Zenon Energy 7.5 and communicating with IEDs using Zenon 61850 Driver through redundant fiber switches (L2 & L1) Also I'm monitoring the switches alarms and port status using Modbus Driver in Zenon. My Srvr (windows 7 Pro) has
Scaling Problem
Hi, I have Volt and Amp data from different IEDs via Modbus TCP and IEC 61850. My problem is: - I need Amp (current) scaling factor to be adjustable by user input in runtime. There should be some code which will pop-up input screen on pressing "Settings"
Gis
Hi Guys I am working related to wind industries. Have some doubts in Editing GIS. 1.How to insert text in GIS (Eg. Name of the Wind Turbine near to the marker) 2.How to insert a variable value in the GIS (Eg. Power and Wind speed of that turbine near
COMTRADE and Motor Start Trending
Hello Support, For Zenon 7.5, the feature of reading COMTRADE file to show the waveforms is there, my question is : for motor start trending which motor protection relay has it, can we show it in zenon using COMTRADE file? Thank you in advance Best regrds.
IEC61850, import variables from driver
When using the "Import variables from driver" for IEC61850 protocol in zenone 7.5 - variables are not downloaded in full. We have access only to the variables available for display (read area) only . Access to a variable with the ability to send control
IEC61850: connection lost but varaibles non updated
Hi, i have a big problem in zenon, in particular in IEC61850 client driver. Driver has 20 connections to different RTUs. Problem appears when I turn off RTU. I will aspect that driver has INVALID status for each variables of that RTU, instead Zenon reads
IEC61850: connection lost but varaibles non updated
Hi, i have a big problem in zenon, in particular in IEC61850 client driver. Driver has 20 connections to different RTUs. Problem appears when I turn off RTU. I will aspect that driver has INVALID status for each variables of that RTU, instead Zenon reads
Command Processing
Hello! I have Double point (DP) commands which I need to switch via command processing. it's obvious how to do it But I've got a problem how to open different command screens for different command direction. I mean: 1 case) I want to switch ON, then I
Zenon 7.11 is incompatible with Multiltin ( 61850 ) Protection Devices
We are currently using Zenon V7.11 as our HMI / SCADA. We cannot get it to successfully get data from GE Multilin G60 and F650 Protection Devices using 61850. The issue is that the Zenon needs to set an integrity period when initialising the 61850 MMS