Symbol corrupted
Hi, during working around a Combi_SWITCH_01 symbol in screen, after a modification that, sincerly speaking, I do not remember, the symbol has become without circle and with a blue cross inside the square and it is disappeared from the General Symbol Library.
command processing for setpoint values, responsvalue question.
Hi I'm using zenon energy edition 8.1 using IEC 60870 driver to a RTU. To write analog setponit values to the RTU, I'm using command processing, one setpoint variable T50 and responsevariable T36. As soon as the T50 value is recieved in the RTU, its looped
INTERN and SIMUL32 driver in Command Processing
Dear zenon support team, I need to integrate several IEDs (relays) using Modbus TCP/IP (Modbus Energy Driver). These IED's are able to control circuit breakers and ccording to its Modbus mapping, there are two boolean signals for open and close status
Show value from a variable coming from an IEC 61850 Server
Hi, sorry if this question is so basic but I am a new user. I just want to know how I can link a variable which I am getting from an IEC 61850 server through MMS to a button of display in zenon so I can see it. The value on the server is connected to
Reaction matrix condition time hysteresis
Hey! I'm working with reaction matrixes in ZEE 8.20 and I'm trying to make it trigger CEL entries with time hysteresis. What I mean is that there is an option called "delay" and it works fine, limit value that I set is not triggered until that state is
IEC61850 - Float32 Variable - Data Type REAL - Unable to use 'Numeric value' element
Hi All, I have been trying to display Float32 variable such as Current and Voltage. However, based on the HELP Section, Tip/Workaround: If you nevertheless want to continue working with the Data type REAL , (such as when there is a limitation of the data
Load Management in zenon Energy Edition
Dear zenon support team, We would like to implement a Load Shedding in distribution electrical system (IEC 61850 protocol mainly). Is it a suitable solution to use Load Management module in zenon Energy Edition in order to fulfill this need? The manual
Commands screen actions not going in CEL
Hello I have an issue where commands (OPEN/CLOSE Breaker) requested and executed from Command screen are going in the Chronological Event List but the operator which have requested the command is not showing in the CEL. Other events executed from the
zenon enrgy edition runtime license
Hello I would like to know the difference beween runtime server license and runtime client license for zenon energy edition. version 8.00 Thank you This is a migrated post! Originally posted on 29.03.2020 by user syous. Please be aware that information
Converting a standalone project to a multi-user project deleted the variables and functions
Hello, We have a standalone project and decided to switch to multi-user operation. However, converting the standalone project to a multi-user project deleted all the variables and functions. What could be the problem? Thanks in advance. This is a migrated
Alarm Message List in Standart Screen Type
Hi Dear Experts, I want to show screen specific alarm lists for each screen. For example I have 21 Medium Voltage Cubicles in one substation. Under the feeder detail pages I want to show feeder alarms, in standart template there is no alarm message list
To Create Realtime Values Calculated in Certain Period of Time
Hi there, Is there a way to create a realtime daily energy variable from the total energy value? I have some devices that only give total energy value which is cumulative and increases every day. And, I want to see the realtime energy value of today on
Reaction Matrix with status bit 53, Zenon EE v8.0
I would like to include status bit 53 (T_UNSYNC) as status value in a reaction matrix, but i can only find T_INVAL amongs the 33 status bit that are available that is related to the time stamp. Is there a way to check if T_UNSYNC is = 1 and add an extra
Systemmessages in eventlist
Hi I have a migrated sicam230 Project running in Zenon 8.10. Whenever Runtime is started or stopped, I get a line in the eventlist saying $ SICAM230 started, or stopped. Where can I change this message to Zenon instead. This is a migrated post! Originally
IEC61850 FileTransfer(COMTRADE) With Dynamic Text
Hi Everybody, When I send the DIR / COMTRADE command for file transfer, I get a long list. I'm trying to display this list with dynamic text, but it's not enough. What can I use instead of dynamic text How can I reverse-view the information that comes
Zenon doesn't see the Report Builder
Hi, We are using Zenon Energy Edition 8.1, I installed the latest version of Report Builder from the Microsoft website. But somehow Zenon can't see it. The RDL files are already defined to Report Builder. I also try older versions of Report Builder and
zenon EE 7.2 iec-61850 communication
For now we have been in trouble to processing YANBU phase 3 project regarding IEC-61850 communications in SaudiArabia 1. a matter for phenomenon>> We are communicating about 100~150 IEDs from one Server by using ZENON EE 7.2 ver.>> While we are communicating
PRP in a SEL computer
Hi Support, We want use COPA-DATA PRP Driver in SEL-3555 computers. SEL computers will run ZEE servers and clients. I see the manual and you said COPA-DATA PRP only works in Windows 10 (and other old versions), but the newest SEL computers runs Windows
Using drivers from zenon Supervisor in SICAM 230
Hi, Is it possible to use drivers from zenon Supervisor in SICAM 230? I need to use MODBUS TCP and SNMP driver. Should I integrate the driver in file Treiber_EN.xml in folder C:\ProgramData\SIEMENS\SICAM230711? Does some on got an experience about it?
Automatic line coloring issue
Hi forum, I need some help for automatic line coloring. I am preparing a scada for switchgear with energy edition. I am using alc, but lines and symbols don't change according to alc configuration. The lines always shows like earthed, but the line is
zenon limitations_project design_reg
Hi All, Now we are planning to design a project for Australian utility, In order to select hardware and software , networking devices we need to know the Zenon limitations. I have tried to get the data in help unfortunately I cannot find it anywhere 1.
Process gateway_iccp_configuration
Hi All, Process gateway ICCP below details were not updated in help, Can anyone clarify 1. General tab-->Server -> VMD specific, Domain Specific 2. Server Variables-->Available for ICCP-->Object type-->Device object I cannot able to get a proper documentation
Need to provide the Engineer in Vietnam
We have demand to find the engineer for our configuration of Zenon Energy Edition in Vietnam. If anyone can provide the engineering fee, pls contact with me - Some document for the reference This is a migrated post! Originally posted on 13.09.2019 by
Hysteresis on Historian Archive
Hello Everyone, I have a question! My IEDs send to Zenon 8.00 some cyclic measurement (2s) from field and I use this data for trend graphs. To preserve data storage and archive of server (10 years average life of the plant), I would like to save the data
MODRTU32 symbolic address
Dear COPA DATA forum members, To sum up the story, I am using MODRtu32 driver, and what I have seen symbolic address is like in IEC - 61850 (please see attachment). Can somenone explain me if MODRTU32 uses symblic address for reading variables ststuse
Convert phase to neutral value to be displayed as a 3 phase value
Hi, I have been looking at how to take a received 61850 single phase voltage value which is all the BCU that the contractor has provided and need to display on the over view the 3 phase value for the engineer. In the past substation the BCU's have always
'Kommando' text instead of Command in Event list
Hello Team, In one the energy project, whenever we are given any command in the event list Text column we seeing "Kommando" instead of Command. I am not using any language files also. Zenon Version 7.11SP0. Also find the attached screen shot. Kindly provide
Facing error of command group even though variables available and linked properly
Hi, FACING ERROR (RESPONSE VARIABLE DOES NOT EXIST) OF COMMAND GROUP EVEN THOUGH VARIABLES AVAILABLE AND LINKED PROPERLY. PFA Screen shot error This is a migrated post! Originally posted on 07.08.2019 by user jameerbashaias. Please be aware that information
redundant iec 104 gateway standby server disconnects
Our system is built around 2 scada servers. Both servers have a gateway function built in (they function as clients). The idee is that different iec104 server paires can connect to our system and get data from us. The servers of our employer works on
Network Authorization for Users
Hi I have a total of 4 systems in a network, I would like to block the execution of breaker commands from the other 3 and only assign oneSystem for the execution. How do I use Network Authorization or is there any other way I can achieve this? All the
Linking Users to corporate Domain account
Hi, Is it possible to use the corporate domain accounts for user accounts in Zenon Energy Edition. If possible please explain how to do it. This is a migrated post! Originally posted on 18.07.2019 by user Xavier. Please be aware that information can be
HMI Panel
Hello all, I have been working with zenon Energy Edition to try and create an HMI panel for a substation. I was wondering if there are any startup guides or manuals for beginners like me available. If you could let me know, I'd be grateful. This is a
Disturbance records (COMTRAD)E IEC 61850
I have several IEDs that I need to read out cometrade files automatically when a new record is created.I will want to use the function file transfer in IEC-61850. Zenon EE 10 supports viewing of cometrade files. But is the predefined script to get the
Command Processing with USINT data type from a DNP3.0TG driver
Hi, I would like to ask on how I would configure command processing for Close/Trip command of a breaker. From the zenon energy edition training that I attended, they have used IEC61850 driver and BOOL data type. Right now, the controller of the breaker
IEC104 General Interorgation
Hi I need to send command GI from Zenon 104 master per hour. In manual that "By creating command execute with TYPE=100, QULIFIER=20 (VALUE=TRUE or FALSE), you can start a general interrogation manually " so this is in command processing. But it can not
Send COMTRADE in an e-mail
Hi Support, I know its possible get COMTRADE files from IEC61850 relays using file transfer properties and also zenon logic (automatic reading). But, if i have already the comtrade file in the Zenon server, could i send this file to an e-mail using ZEE,
IEC60870-5-104 Settings for redundancy with Sicam AK3
Hello I have one standalone Zenon runtime PC, Communication via IEC60870-5-104 with one redundant Sicam AK3 system, (consisting of tho AK3 with internal voter logic). My settings on the Zenon driver are these: Redundancy according to Edition 2.0. Communication
Problem with ReMa, 61850 Report communication and delay time
Hello, I have a problem with delay in reaction matrix in zenon energy 8.00. I'm using a 61850 driver with Report Enable (All my data points are tagged with COT0, COT1 ). I configured a Binary Rema with a short delay (5s) to create a new entry in alarm
geographic information system in Zenon
hello support, I need to use kMZ files but I do not know if the Zenon has the GIS functionality. Please indicate if it is possible to make such an implementation and how you could do it. regards This is a migrated post! Originally posted on 29.03.2019
Zenon Logic to check if a Zenon Variable is online
Hello everyone! I'm using Zenon Logic to check if a 61850 variable on Zenon (External Visibile) is Invalid through VsiGetBit IsInvalid := vsiGetBit ( {QSACC!QSACCUPCIN/DP8GGIO6/DPI1/stVal[ST]}, 18 ) But in the first 10 seconds of start of the Runtime,