MODRTU32 - Preset Multiple Registers (FC 16)
Dear Forum Community, I am using MODRTU32 driver in order to integrate some IED's in MODBUS TCP/IP. To execute commands I need to write two registers at the same time and when I create a new variable I only find the option 'Preset Single Register (FC
LON Treiber - aktueller Stand
Hallo zusammen, inzwischen ist ja zenon Version 8.10 erhältlich. Ist da inzwischen auch der LON-Treiber aktualisiert, sodass man auch OpenLNS anbinden kann? - Ich würde an dieser Stelle nur allzu gerne von dem alten OPC-Server wegkommen, der seit Windows
Hysteresis / Deadband for process gateway signals
Hi, I'm trying to achieve a 'deadband' on analogue inputs sent via DNP3 outstation from process gateway. Support have confirmed that PG doesn't have such a feature so I have requested that be added to roadmap for future. In the meantime I'm trying to
Reading Values with the DDE-Driver from Excel
Hi! I am trying to read a column from an Excel-table into an array in zenon. In order to do that I created a DDE-Client-driver and a DDE-variable. Name: EXCEL_Value Server: EXCEL Topic: [AUFTRAG.XLSX]SHEET1 Item: R1C1:R8C1 Then I imported the variable
IEC 60870-5-101 Line Redundancy
Hi, We are designing a SCADA system for substation with Zenon Energy Edition V8.0. Client wants that, SCADA will get signals from field devices with IEC60870-5-101 protocol. There are 2 serial ports on the computer and also field devices have 2 serial
MATHDR32 counter variable problem
We have system with 2 redundant servers ver. 7.0 and 2 clients. We count working hours for few machines using MATHDR32 variables that are recorded in historian. After a accidental power loss the servers restart and some (not all) of the counter variables
Straton/ModbusTCP driver - How to set parameters?
Hello. I'm trying to set a tcp port and ip address in a modbus tcp slave driver. In the driver configuration are not fields. This is a migrated post! Originally posted on 26.04.2019 by user mhanusek. Please be aware that information can be outdated.
CEL doesn't record events when loss of connection to RTU
Hello, I've had some problems with getting events from an RTU when the RTU loses connection. The connected RTU stores the change of events when it looses connection to it's OPC gateway, zenon connects to the OPC gateway as an OPC DA client and reads the
Zenon Driver cannot register
Hi, does anyone know why there is an error of BECKHBC32.exe cannot register and Beckoff BC-BK 9000 cannot start during runtime start up. Any solutions for these problems? Thanks This is a migrated post! Originally posted on 04.03.2019 by user shaun. Please
Modbus energy driver
Hi, does anyone can help on this issue? Thanks This is a migrated post! Originally posted on 25.02.2019 by user shaun. Please be aware that information can be outdated.
Remote OPC DA Server with Zenon OPC Client
Hi, We have to connect a Zenon Supervisor (OPC DA Client) with a third party SCADA (OPC DA Server) in the same network (actually there will be connected in the same ethernet switch). I was reading the manual and you donÂ't recommend use OPC Client in
OPC-UA Variable: externe Zeitstempel eingefroren
Hallo, Ich bin in der Planungsphase einen OPC-UA Server auszulesen und prüfe die Machbarkeiten ab (es werden mehrere tausend Störmeldungen mit zeitrelevanten AML/CEL/Archivierung/Message Control). Ich habe ein Problem mit dem externen Zeitstempel von
ESPA-X Anbindung
Hallo, gibt es eine Möglichkeit zenon an das ESPA-X Protokoll anzubinden? (https://de.wikipedia.org/wiki/Erweitertes_Signalisierungsprotokoll_f%C3%BCr_Alarmprozesse#ESPA-X) Einen Treiber habe ich hierzu in der Hilfe leider nicht gefunden. Wir benötigen
OPCUA: Changing the parameter QueueSize for a monitored item
Is there any way to change the queueSize for the monitored items. I have checked via wireshark: RequestedParameter QueuSize is everytime 1. This is a migrated post! Originally posted on 25.01.2019 by user savenni. Please be aware that information can
OPC DA Server- Client Configuration
Hello, HMI : IPC with Zenon 6.51 SP0 PLC : PacDrive C600 Client : Third Party Software I am new to the Zenon OPC server configuration, i would like to ask, For OPC DA configuration, 1. Which Tunnel software to be used for communicate between Server and
S5TCP32 - Keine Verbindung zu S5-CP
Hallo, ich möchte mit S5-Steuerungen mit Softing S5TCP100 eine Verbindung mit Zenon 8.00 und S5TCP32-Treiber herstellen. Leider habe ich keine Erfolg. Ein Test mit einem Softing-OPC-Server zu den S5-Steuerungen war erfolgreich (Port 5000 und 6000). Ich
Zenon 6.51 OPC Server Configuration
Hello, Can anyone please share manuals for configure OPC UA Server in Zenon 6.51 runtime. I have to transfer data with OPC UA from Zenon 6.51 to client side Scada. If anyone have sample project, please share.... This is a migrated post! Originally posted
WMI Treiber
Moin, gibt es eine Möglichkeit / Treiber eine Schnittstelle zur Windows Management Instrumentation (WMI) zu schaffen? Wir haben ein Netzwerk, in dem nur einzelne MAC-Adressen freigegeben sind. Wir würden nun gerne eine Meldung in der Ereignisliste oder
Maximum Number of bytes will be polled (Read) by zenon in S7TCP driver - Profinet network for each priority (Normal, high, higher, highest) variables
Hello Team, I want to calculate the variable update (read) time by zenon based on priority set for more than 1000 variables. i.e. how much time it will take to update the variable value in zenon for variables which are prioritized as Normal, high, higher,
Driver Mode Switching recommendation?
Dear Team, I'm using Zenon 7.50 Build 49034 and multi-project structure with Three different drivers. I want to stop communication when no communication from controller kindly suggest Driver Mode switching Functions 1.For starting Driver ----> a) Driver
Siemens PLC to Zenon - Variable update time delay in S7TCP driver - Profinet network
Hello, In my project i am using Siemens CPU 319 and in zenon S7TCP driver was used to communicate with PLC in Profinet network. Total 4200 PLC variables are created in Zenon. Out of 4200 variables 1200 variables are used as permanently read variable.
Unsolicited DNP3 Communication with Zenon 8.0
Dear Support, I am getting the unsolicited messages when my RTU connected to in ASE Tool as Master. However, I am unable to get the Unsolicited message frm same RTU in Zenon runtime v8.0 . I am attaching the Zenon DNP3.0_TG Driver setting i did, for your
SNMP Driver memory issue
Hello Support, I have one doubt for SNMP driver, How many IED we can add in single SNMP driver ? A large memory (CPU & memory) used by this driver. I want to minimize it. For Example, I have 16 switch, so how many driver i have to create so that system
Zenon Remote Runtime Driver Issue
Dear Team, i have been trying to communicate to low version to High version and vice-versa. Having more problem in Zenon 7.50 ,7.60, 8 version After multiple trails then communication is being establishing. Provide solution as soon as possible Regards
Autmatic write command at the every new start of Modbus TCP session
Hello! I am trying to communicate with diesel controller via Modbus TCP from Zenon EE 6.22 SP1 Build 0. Controller type is ComAp IG NTC BB. At the start of every new Modbus TCP session there must be (multiple) write command to ceratin register(s) in diesel
Create Custom Driver
I want to create a custom driver to connect the Zenon PC to another PC with TCP/IP via ethernet. The driver is created with zenDrvHelper and edited in C++ Visual Studio. The problem is there isn't any manual book to create custom driver, especially TCP/IP
DNP3 communication
Hello, I have question about DNP3_TG driver. I want to create communication with RTU (DNP3 Slave) via GPRS TCP/IP. But wap ip address of the outstation is not static. The case is that the slave initiates a session but the master does the polling so Zenon
Delta PLC AS300
Dear reader What driver is needed to integrate a Delta AS300 PLC into the Zenon SCADA? The Delta AS300 utilises Ethernet IP. Thank you kindly This is a migrated post! Originally posted on 11.08.2017 by user PaulRudolph. Please be aware that information
DATEI32 File Driver
Hello, I want to import data from "data" (csv) file To Zenon archives. One solution proposed from our local support is to use file driver "DATEI32 (but they didn't try) From help file : "The file driver supports the data exchange between zenon and an
Problem with Treiberkit760_SP0 when creating new driver
hello i have a problem with Treiberkit760_SP0 when i generated driver using zenDrvHelper.exe in directory D:\Treiberkit760_SP0\zenDrvHelper , on documentation DriverKit.pdf, Treiberkit710_SP0 is different folder structure when i got. when i compiled mydriver
Communication Problem with Simens S1500
Good morning, I write because I have a problem with the communication between PLC and Zenon Runtime v7.50 installed on an industrial pc with Win7 x86. I've alredy set up the driver (S7-TCP IP) with the correct CPU adresses, put the remote TSAP 02.01,
IEC61850 Driver - Connection State
I'm working on Zenon Operator 7.50. I have define IEC 61850 Driver with 4 server (ref to fig). Everything is working fine. My question is: where can I find the connection state of each server? in which variable? Thank you, Andrea This is a migrated post!
Driver Simulation Project - 61850 variables
Hi, I have a Zenon project in which there is a 61850 driver, with its own variables (variables name according to the standard). I want to use Driver Simulation Project, so in driver property I activated Mode: Simulation - Programmed. Problem appears in
IEC61850 Driver - Report control blocks - Communication Problem
I'm working on Zenon Operator 7.50. I have read IEC850 Zenon Driver Manual. I need to connect to a device via IEC61850 protocol. I detected 2 different working case: CASE 1: if my device doesn't include REPORT CONTROL BLOCKS -> ZENON reads variables from
IEC61850 Driver - Data Type
Hello everybody, I'm working on Zenon Operator 7.50 In my project I need to connect N devices of same type. Each device is defined in Zenon like 61850 server with different net address. I'm using symbolic addressing and the import of variables from driver
Mitsubishi fx-5u plc communication
CAN ANYONE KNOWS WHICH DRIVER USED FOR MITSUBISHI IQ-F (FX-5U) PLC ,AND SEND THE BACKUP OF PLC AND SCADA This is a migrated post! Originally posted on 16.10.2017 by user saikumar. Please be aware that information can be outdated.
Modbus Slaves keine Verbindung
Hallo Zenon-Team, ich habe ein Problem beim Abrufen von Prozesswerten über Siemens Energiezählers vom Typ PAC 3100 welche als Modbus Slave an einem PAC4200 als Gateway hängen. Wenn ich den Modbustreiber so konfiguriere dass das Gateway als Netzadresse
IEC61850 Driver - Time Synchronization AML CEL
I'm working on Zenon Operator 7.50 In my project there are two type of 61850 IED device, both can support SNTP synchronization. In the pc where Zenon is running the changing of summer time is disabled and time zone is set +00:00. In AML and CEL Received
Driver priority within UDT
How does driver priority work with regards to variables that are actually elements of a single structure in the PLC? We're using the Logix_ODVA driver, and virtually all of our variables are structured under a single tag. i.e.: BaseTag.Group1.SubGroup1.VarName1
zenon driver für OTPP Protokoll - Cars charging station
Hallo, können sie mich informieren ob dieser "Standart" bei Stromladung für E-Autos bei Copadata entwickelt wird ? Danke. This is a migrated post! Originally posted on 20.11.2017 by user Jusufs. Please be aware that information can be outdated.