Communication problems with Logix ODVA Driver
Hello, I am using Compactlogix PLC and Zenon Editor Version 7.50 for my application. I created the driver and I am able to import variables from PLC. However, when linking some variables from a PLC AOI to momentary buttons I got red dots in the buttons
MODRTU32 Timeout bei TCP/IP
Hallo zusammen, die meisten unserer Steuerungen sind über ModbusTCP mit dem zenon-Projekt verbunden, unabhängig davon, ob sie am Gerät Modbus+, ModbusRTU oder direkt ModbusTCP können. Das geht alles wunderbar über Bridges und Gateways. Dennoch haben wir
Configuration of IEC60870-5-101/104 Driver in SICAM 230
This is probably a "newbie" question, but I am unable to find any information on how to configure the IEC 60870 driver (Siemens IEC60870-5-101/104 (AKServer) Driver) in SICAM 230 version 7.20 SP0 Build 24121. Is there a manual, help or anything describing
Can not get variables to Zenon ( v7.2) from S7-1200
Hi everyone I have trouble about comunicate between Zenon and S7-1200. I need see variables in Zenon (v7.2) when connect S7-1200 but I can not add this. I read help online and see it does not support browing online. Then I try to browing offline but I
OPC Funnel Wrong connection
Hi I am using a OPC and i am try to connect but i cant. I am using Matrikon OPC Funnel See above the printscreen. How should i do? This is a migrated post! Originally posted on 15.03.2017 by user marcelodias. Please be aware that information can be
IEC62056 / TCP/IP problem
Hi, I use SICAM 230 and need to read data from energy meter ISKRAEMECO MT830 over IEC1107 (IEC62056) TCP/IP. I can connect to the device using telnet and I have ISKRAEMECO software installed and it is connecting to the meters like this: I edited file
Siemens Logo
Moin, ich wollte mich mal erkundigen, ob es eine Möglichkeit gibt eine Siemens Logo auf die Zenon aufzuschalten und was genau ich dabei zu beachten habe? Also welcher Treiber zu verwenden ist (S7 TCP/IP) oder einen anderen? Gibt es bei dem Zugriff auf
Zenon v7.20 unable to communicate with S7 1200
Hi i am trying to comunicate with the PLC 1200 and i cant what should i do? This is a migrated post! Originally posted on 23.02.2017 by user marcelodias. Please be aware that information can be outdated.
Zenon OPC UA Client driver
Hello, i tried to connect the ua Client Driver with the OPC UA Server of a Simotion. However, while importing variables from the Server a error message pops up with the Content: "Failed to evaluate data types at SIMOTION! Failed to read data types: The
Treiber startet nicht mehr
Hallo, ich habe für jeden bei uns verwendeten Treiber die Treiberfunktionen für Start und Stop, Hardwaremodus und Simulation auf Buttons gelegt, um diese im Fehlerfall oder bei Umbaumaßnahmen besser im Griff zu haben. Gestern habe ich im Zuge einer Umbaumaßnahme
Bacnet Treiber
Hallo, folgendes Bacnet Problem (bei allen 7er-Versionen): Mit dem Treiber Bacnet und DDC4000 Treiber (1) kann ich problemlos Variablen importieren. Standardeinstellungen, Trennzeichen für Propertynamen ist ein Punkt. Mit dem Treiber BACnet Treiber Next
SIMUL32 Driver
Hello everyone, This is my very first post and as a newbie go easy on me please :) Our factory has a machine with S7-400 cpu, controlled by ZENON scada. In ZENON scada project there is a bit parameter which apply new setting to cpu but it(switch) connects
Mbus Treiber
Hallo, ich betreue ein sehr altes zenon-Projekt, Version 5.50 SP7. Ich habe hier zwei baugleiche Elektrozähler angelegt: Einen Zähler kann ich problemlos einlesen, den anderen nicht (Adressierung etc. stimmt alles). Integriere ich testhalber das Projekt
Edit driver modus outside the editor
Hello, we are trying to modify the mode of some drivers inside a project from "static" to "Simulation - programmed" without having to use the editor (Dynproperty "GenDriverMode"). If that were possible, we would be able to execute the runtime from a project
Modbus Energy Driver // MiddleEndian
Hi, I want to set up a Modbus TCP connection using the MODBUS ENERGY driver. The device I want to connect to, has its data available in Middle Endian format. Big Endan= B1 B2 B3 B4 Middle Endian: B3 B4 B1 B2 In the Modbus Energy driver, I can only choose
DNP_TG Issue
Hello Support, In on of our projects we are using DNP_TG driver to communicate with GE RTU serialy using RS485 2 wire, all configuration we did is fine and the communiaction also was fine, after time we lost the communication and it is giving error in
Treiberkonfiguration Export/Import XML
Hallo, habe Frage zu dieser Möglichkeit. Wenn ich nämlich zahlreiche Unterstationen in meinem Vorab Projekt definiere und möchte die Arbeit ins Scharfprojekt einbinden, muss ich die Verbindungen zu den Unterstationen händisch neu anlegen. Gäbe es dazu
B&R PVI Treiber
Hallo liebes Zenon Forum, ich habe ein Problem mit meinem PVI Treiber von B&R. Ich würde gerne Globale Variablen von B&R importieren (œber die Online Importfunktion am Treiber). Doch hier sagt mir Zenon ich muss neben dem Verbindungsnamen auch einen Tasknamen
Siemens Simotion Treiber Variablenimport
Siemens Simotion V4.4 D445 -- Zenon 7.5 Gibt es eine Beschreibung für den Treiber? Wie muss die STI Datei aussehen? This is a migrated post! Originally posted on 30.06.2016 by user MNM. Please be aware that information can be outdated.
3S Arti NG - Problem mit Strings
Hallo, kann es sein, dass es mit der Ver. 7.50 Supervisor ein Problem beim Schreiben von Stringvariablen gibt? Lesen funktioniert, aber sobald ich die Variable beschreiben will wird der Inhalt auf der Steuerung (Eaton) gelöscht!:confused: Grüße Johannes
Snmp
Hello support, For one of our projects we are using 7.2 and SNMP driver to monitor the switch ports, SNMP driver communicating but after some time the communication is lossing with SNMP, and when we try to read the MIBs again from switch it dose not reading.
Array mit BeckhNG einlesen
Hallo zusammen, ich mache gerade das erste Projekt mit dem Beckhoff Treiber sonst immer S7-TCP/IP. Wie kann ich mit dem BeckhNG - Treiber ein Array[1..64] of Bool einlesen über die Symbolische Addressierung bzw. besteht die Möglichkeit das ich eine ganze
Can not find Verbindungnamen in Zenon editor Version 5.5 SP7
Hello, I have a problem with Zenon v 5.50 SP7 that I can not find the Verbindungnamen in the S7 NT - S7 300/400 driver See attached file please! Iamge 1 At Image 1 you will see that the S7 driver could not be able to show " zenOn" application and you
Reading a REAL with Modbus tcp/ip with EWON
Good Day I have been having a struggle with reading a REAL value by using a Modbus Driver. I am connected to an eWon device and when I publish a specific register in the eWon software and read it with the corresponding offset in Zenon it works for Integer(Holding
BACnet Priority-Array Variable anzeigen
Hallo zusammen, Ich baue mir da ein GLS zusammen. Schreiben und zurücksetzten von Prioritäten habe ich Erfolgreich gelöst. Jetzt ist meine Frage, wie kann ich anzeigen wenn eine Variable von Hand (Prio 8) geschrieben wird? Besten Dank für Eure Antworten
Retrive Data via Bacnet/IP protocol
Dear Sir, Currently we are doing some testing trying to retrieve data from Digital Power Meter (Modbus) via Bacnet/IP. Somehow, we unable to retrieve the data like voltage or current. How are going configure our driver configuration and the variable setting?
ODBC variable show
Hi, I have a sample database in MySQL. I successfully setup the connection between the database and zenon using the sqldrv. I want to show a text from the database on the screen when I use runtime. I have imported a variable with the same exact name from
PDIAG alarms with dynamic text
Hello, I hope that you can help me in the following matter. We were requested by our customer to modify the existing Zenon project (v6.51). The modification includes the alarm display with dynamically changing text. Currently alarms are generated in PDIAG
Driver from Hardware to Simulation
Hello, I would change modbusrtu driver mode at runtime from HW to Simulation. It's possible? zenOn 7.0 SP0 Build14 driver ModbusRTU (TCP/IP) If I have the automation that is communicating and I run HW_to_SIMULATION function everything seems to work properly.
Wago 750-8202
Hallo! Wir möchten mit einer SPS von WAGO über TCP kommunizieren. Typ 750-8202(/xxx-xxx) PFC200 CS 2ETH RS SPS - Controller PFC200 Hat jemand Erfahrung mit welchem Treiber und mit welcher Adressierung wir beginnen können? Ich habe den Modbus Energy Treiber
Zenon OPC UA client out of memory
Hi, When importing a big amount of OPC tags from an OPC server, the Zenon OPC UA client 7.20 crashes with an out of memory notification. Is there a way to manually insert a selection of tags in the OPC UA client without first importing all the available
Hohe Latenz
Hallo, ich habe bei zenon 7.20 eine sehr hohe Latenz. Ich benötige Echtzeitdaten, meistens ist es jedoch so, dass die Signale mit Verzögerung umgeschaltet werden (Vergleich mit dem SPS Programm, welches parallel beobachtet wird) und Funktionen nach einer
how to connect melsec plc Q13UDEH by cpu module ethernet port
i want to connect mitsubishi melsec PLC (Q13UDEH) cpu ethernet port. i followed the driver manual, but i failed. how to config zenon driver? This is a migrated post! Originally posted on 13.10.2015 by user miki72. Please be aware that information can
3S Arti NG Treiber - Kommunikationsproblem
Hallo, habe folgendes Problem mit dem 3S Arti NG Treiber (Zenon Supervisor 7.20): manchmal, wenn die Steuerung ausfällt (Stromausfall, Schaltschrank ausgeschalten...) bekomme ich nachher keine Verbindung mehr. Das Problem lässt sich beheben indem ich
DB einstellen in S7TCP32
Hallo zusammen, ich stehe gerade irgendwie auf dem Schlauch :confused: Ich soll von fünf externen Siemens-CPUs jeweils aus dem DB100 ein paar Bits auslesen. Nach meinem Verständnis müsste das über den S7TCP32-Treiber funktionieren. Jedoch bleibt bei mir
Save to SQL server every 3min
Hello everyone! I am wondering if it is possible to save the data to SQL server every 3 minutes or so. I do not want to increase the update time on S7 TCP-IP driver though. I tried increasing the time on SQL Driver, but it keeps sending the data at the
communication with s7
hi; I have problem connecting zenon with s7-400 using PC-Adaptor, I have zenon, HardLock doungle and PLC, what step do I have to do for having comunication? thanks This is a migrated post! Originally posted on 02.09.2015 by user ameic. Please be aware
TreiberAnbindung mit Modbus zu ein Janitza UMG605 Messgerät
Weiß einer wie man zu einem UM605 (von Janitza) über Modbus zugreifen kann ? This is a migrated post! Originally posted on 20.07.2015 by user hare1268. Please be aware that information can be outdated.
Zenon 7.11 mit SAIA PCD2 koppeln,
Hallo zusammen! Wir haben in unserem Betrieb mehrer Lüftungsanlagen die alle von einer SAIA PCD2 gesteuert werden. Angeschlossen haben wir die SAIA mit TCP/IP und können darüber über das Netzwerk mit der SAIA PG 5 2.1 Suite aus unserer Werkstatt überwachen,
BeckNG: Adresseparameter (iGroup...) bei symbolischer Adressierung notwendig?
Hallo! Ich beschäftige mich gerade mit der automatischen Erstellung von zenon Projekten per VSTA. Nun bin ich beim Anlegen von Variablen und deren Adressierung für den Treiber BeckNG angelangt. Die Frage ist nun, brauche ich die Adressparameter der Variablen