Recent Topics
alarm page buttons
hi there! ive noticed during RT most of buttons in alarm page are disabled (like acknowledge button, acknowledge all button, delete page button, delete all. button, etc), alarms are being shown in the page but i cannot acknowledge it due to disabled buttons
TCP/IP Comm problem
Having problem communicating with S7-400 Siemens PLC. I have created three projects in the past, so this is not new to me. I can ping the processor and connect using STEP7. I've tried deleting and re-creating the driver and the variables. I'm still getting
alarm status from variable
HELLO i'm writing some macro. I have a variable, and i need to know if it's value is alarm or no and if it is alarm if alarm of variable is Acknowledge. I use REMA for variable stati.:confused: This is a migrated post! Originally posted on 05.10.2009
search replace variable text
Im trying to search and replace the following: @V401!AWWG401A@@ by @V405!AWWG405A@@ search string V401!AWWG401A replace string V405!AWWG405A zenon does not recognise the search string. Am i doing something wrong Can anybody help me Im using 6.22 SP1 build5
ALC interlocking
Hello! I would like to use ALC interlocking "Disconnector under load", but it seems it does not working OK for my purpose. E.g. I have a disconnector which is supplyed only from one side. On the other side it is undefined (not supplyed) and I get the
RGM-Rezeptgruppe online ändern, Auswirkungen auf bestehende Rezepte ???
Was passiert mit bereits gespeicherten Rezepten wenn man die Variablen der Zugrunde liegenden Rezeptgruppe online verändert. Mögliche Veränderungen: a: es kommen Variablen hinzu. b: es entfallen Variablen. c: die Position von Variablen ändern sich. d:
Remove double scrollbar in Zenon WebClient
Hello! I wanted to use the scroll option in the init.htm to provide scrollbars for smaler screens but now i am also getting seccond scrollbar on each side wich looks realy ugly. Is there any way to get rid of that one? This is a migrated post! Originally
Weltbild - Bilder stimmen nicht mehr??!!
Hallo, wir haben ca. 6 Bilder die alle zusammen eine Anlage ergeben. Hier haben wir uns nun eine Weltbild Darstellung "gebaut". Nun das Problem: Wenn ich die einzelnen Bilder/Anlagenteile markiere, STRG+C und ins Weltbild einfüge. Klappt alles einwandfrei,
Normal status (NORM)
hello i have set variable "normal status" active on and normal value ON but Normal status (NORM) bit always is "0". Where is the problem?:( This is a migrated post! Originally posted on 30.09.2009 by user westbaaam. Please be aware that information can
ZenOn RT starting before TwinCAT on CE
Has anyone come accross a situation where ZenON RT process is starting for TwinCAT on a CX1020 CE5.0. On Boot up ZenON is VERY slow, if we close the RT and open it again then it runs fine..... Thanks dcg This is a migrated post! Originally posted on 29.09.2009
VBA Makro wird nicht Abgearbeitet
Hallo zusammen, Habe ein Makro geschreiben für nicht lineare Wertanpassung, dieses funktioniert auf meinem Rechner einwandfrei. Das Problem liegt daran, wenn ich es im richtigen Projekt einsetze funktioniert es nicht. Da das Makro nicht abgearbeitet wird
Mehrere Rezepte gleichzeitig Laden/Speichern
bin jetzt bei der VBA - Lösung. Rezept anlegen in der entsprechenden Rezeptgruppe geht. nur bekomme ich die aktuellen Werte der Variablen nicht ins Rezept, wobei VBA ohne Fehler durchläuft. VBA- Code Dim zRecipe_Group_Name As String Dim zRecipe_Name As
Client runtime licensing
In our project, it is assumed that each client uses only some of the server variables. Is it possible in this case, that client license may be fewer in variables number than for the server (for example, the server 16384 tags, clients 8192 Tags each)?
Reading "M" bits in Siemens
Is Driver Object Type "PLC Marker" to be used to read "M" bits in Siemens processors? This is a migrated post! Originally posted on 23.09.2009 by user scotttee. Please be aware that information can be outdated.
Zeisteuerung über VBA ändern
Hallo zusammen, besteht es die Möglichkeit eine Zeitsteuerung während die RT läuft zu ändern über VBA. Bräuchte das für den Export von Dateien damit der Kunde sich selbst die Interfalle einstellen kann. Wünsche noch einen schönen Tag. This is a migrated
Zenon 5.50 SP5 Demo Version Needed
Hi, i've been wondering if a demo version of Zenon 5.50 Sp5 is available to download ? I've got a project in that version and i cannot convert it to newer due to clients needs. This is a migrated post! Originally posted on 22.09.2009 by user adf_kdm.
RecipeName combo-box
Hello, i'm searching for a similar problem in this forum but didn't find anything yet... here what i would like to do: > in a Recipe synoptic, i have implemented the RecipeName combo-box > as soon as the user selects an entry from this combo-box, the
Scale
ist es möglich, die Skalierung einer Variablen z.B. mittels einer booleschen Variablen umzuschalten um z.B. die Ein- Ausgabe eines Werters zwischen mm und Inch umschaltbar machen. Also mm Eingabe: Wert in der Steuerung 1000 - Eingabewert 1000 Inch Eingabe:
Ungültiges Argument bei Funktion Rezept Manager
Hallo Ich will ein Rezept (Zenon 6.22SP0), welches im Rezeptgruppen Manager erstellt worden ist beim Runtime Start direkt laden. Dazu verwende ich die Funktion Rezept Manager. Sobald ich nun das Rezept anwähle und OK klicke erscheint ein Message Fenster
Interlockings (Verriegelung)
Hello, I have 1 picture that i call on more times with the Function "picture switch" and a filter for variables. Now i have the following problem: In the picture i use a Interlocking (Verriegelung) for a Button. But the variable for that Interlocking
Mehrere Rezepte gleichzeitig Laden/Speichern
Habe die Herausforderung das ich mehrere Rezeptegruppen gleichzeitig laden und auch speichen muß. Es gibt ca 16 verschiedene Rezepte, diese wurden im RGM in entsprechenden Gruppen angelegt. Gibt es eine Zenon Interne Funktion die es ermöglicht aus den
Web Server Functionality
Hello, Some questions regarding web server. 1. There are 2 types of web server licensing: Web Server and Web Server Pro. The normal version offers a view only page view, while a Pro version allows operating actions (control). Is it possible to have Web
Same Project On Two Machines
Hi, I want to deploy the same project on two PC's. There is and keyswitch at one PC which will determine which PC can use a certain page (The page is for starting and stopping the system). The projects communicate to the same PLC and are networked together
Benutzerverwaltung in Runtime
Hallo Ich möchte in der Runtime ein Benutzerverwaltungs - Bild erstellen, welches das hinzufügen, ändern und löschen von Benutzern, inklusive Rechte- und Passwortvergabe erlaubt. Gemäss Help und einigen Beiträgen sollte dies mit Zenon 6.22 nicht nur im
Picture switch - Replace indices
Hello, I have a Picture that i want to use with different tags. When i create a new function "Picture switch" , there is a filter for variables. For example: KFSUA04 must be KFSUA02 AND LS452 must be LS264. (Variable KFSUA02.......LS264 exist!) How can
VBA Timer
Hello, How can I make a timer in VBA? I think there is no timer control in VBA, but also Application.Ontime, which is working in Excel VBA is not supported in zenon VBA. This is a migrated post! Originally posted on 10.09.2009 by user hansvanzijp. Please
Compatibility with Win2008 Server
Hi there. Is Zenon-Copa Data ver. 6.22 compatible with the new OS - Windows 2008 Server? This is a migrated post! Originally posted on 07.09.2009 by user michaelagito. Please be aware that information can be outdated.
CEL & Alarm files on CE
On a CE (6.22 SP0) target project, with activated AML and CEL, I created a standard "Alarms : Save AML and CEL memory buffer" function activated by hand (assofar). However... :eek: no files are created on the target's directory ('SDMMC Card[I]HMI[/I][I]Panel_Name[/I][I]Project_name[/I]\').:(
Universal Regler mit Touchbedienung
Hallo! Ich möchte den Universal Regler in einem Projekt auf einem CE-Panel verwenden. œber den Universal Regler soll ein Sollwert per Touch verschoben werden können. Der Zeiger im Universal Regler mit dem der Sollwert verschoben werden kann ist leider
Modbus read input status
We are trying to read 8 discrete inputs from a modbus device. Input are connected to 8 BOOL zenon variables, using INPUT STATUS driver type and BOOL data type. We have noticed that if we define an array of 16 BOOL associated to the first 16 input register
Projektsicherung von 6.22 SP1 in 6.22 SP0 einlesen
Hallo zusammen! Ich habe ein kleines Problem... Wie kann ich eine Projektsicherung aus 6.22 SP1 in 622.SP0 zurück lesen. Ich weiß es geht NORMALERWEISE nicht, der Editor verweigert den Import in 6.22 SP0 aber es gibt doch bestimmt einen Trick in der Schublade
Online Variable
Hallo Zusammen, Ich möchte in einem Makro eine OnlineVariable erzeugen, welche mir den Wert einer von mir angelegten Variable unter "Variablen" zurückgibt diese möchte ich selben makro gleich weiterverarbeiten und am ende den Objektkontainer auch gleich
GOOSE messages in STRATON
Hello, Is ther any option in Straton to configure SCL files (*.icd, *.cid, *.scd) in straton with reference to IEC 61850 . Also any option to configure GOOSE Rx and Tx. This is a migrated post! Originally posted on 29.08.2009 by user mansoorhussain. Please
Authorizations
I've created a user "oper" and set the authorization level/group to 22. I've set the authorization level to certain elements to 22. After logging in as oper and clicking on a "secure" element, I get the following message: "You are not entitled to execute
Default Kontrollelemente über VBA
Hallo zusammen, wie kann ich über VBA den Refresh Button eines Reportbildes ansteuern bzw. auch die anderen Default Kontrollelemente. Danke! This is a migrated post! Originally posted on 27.08.2009 by user dftchristian. Please be aware that information
Automatic Logout
How do I automatically logout a user after a certain amount of time has passed? This is a migrated post! Originally posted on 26.08.2009 by user scotttee. Please be aware that information can be outdated.
Server redundancy
Some queries on system redundancy. In zenOn, we can have dual redundant servers, 1 server as Main, the other 1 as Standby. In normal operation, the Main server will be responsible in polling the PLC. Does the Standby also polls the PLC at the same time?
How to set column width for Arhive revizion
Hello, How to set for Arhive revizion column widths in the arhive LISTBOX for the display in Zenon Editor? This is a migrated post! Originally posted on 25.08.2009 by user captain. Please be aware that information can be outdated.
What'™s the reason for freezing the value of dynamic element?
What’s the reason for freezing the value of dynamic element? One problem has been occurred in my project,as when I disconnect the plc connection to PC(disconnect the communication connection) the values of dynamic element is freezed in latest value
How to create a "Time Counter" variable?
Hello, As the title, How to create a "Time Counter" variable? When the event is active, the Time Counter variable runs; and when the event is inactive, the Time Counter is reset to zero. Regards, Peng This is a migrated post! Originally posted on 24.08.2009