Under specific circumstances the DNP3 outstation in the process gateway sends an incorrect timestamp that is off by exactly one second
The DNP3 process gateway incorrectly adds 1 second to the timestamp if the milliseconds portion of the timestamp is greater than 500ms.
An issue has been addressed in the DNP3 process gateway where incorrect rounding added one second to the timestamp.
Issue Number: 33625
Fixed on Date: 3.2.2015
Versions: 7.50 0 BUILD 25796
From time to time, at 000ms, zenon Process Gateway sends values with incorrect timestamp.
Summary From time to time and only when variable timestamp has 000ms, the zenon Process Gateway (e.g. IEC870 Slave) sends incorrect timestamps with 1 second back in time. Description From time to time and only when variable timestamp has 000ms, the ...