Under certain circumstances alarms hang / are still pending when a server redundancy switchover occurs and the primary server is in "not responding" state.
Alarms that have already been acknowledged and are gone continue to be displayed in the AML in some constellations. This behavior has been modified.
When a server redundancy switchover occurs and the primary server is in the "not responding" state, some alarms that have already been acknowledged or are gone continue to be displayed in the AML,
Cause:
Since spontaneous values and alarm inputs from standby are received in different telegrams, they may differ. If the main thread on the server is blocked for a longer time, the standby receives the spontaneous value, because the value distribution is done in a worker thread. However, it does not receive the corresponding alarm event because the alarming is done in the main thread. Therefore, at the standby the violated limit is already reset to 0, while the corresponding alarm event is lost. This leads to a mismatch between the current violated limit on standby (correct) and the alarm ring buffer on standby ( outdated).
Solution:
The alarm ring buffer is cleared after the standby server is switched. If a pending alarm is found for a variable for which there is no longer a limit violation, it is cleared. An entry is also created in the DiagnosisViewer.
Precondition: The main thread on the server has been blocked longer than NetworkTimeout/2 immediately before the switchover. Otherwise, alarms during the switchover are handled correctly with the standby buffer. However, the standby buffer buffers value changes only for the duration of 3/2*NetworkTimeout.
Item ID: 267322
Version: 12.00 Build: 159727
Version: 11.00 Build: 161931
Version: 10.00 Build: 159736
Version: 8.20 Build: 160083
    • Checklist: OPCDA Server
    • client in hang state after server ends during file alignment
      Description Client got stuck after the server shut down during file alignment. This occoured when: a network project with a single server was used and a variable from intern driver with calculation "local" and a limit that is violated at start up. ...
    • FAQ: What are Installation and Security considerations of the zenon Smart Server and Smart Client?