BACnetNG driver does not properly write schedule objects
An scedule in BACnet can have the objects:
Device_0030de091099.SCHEDULE_0.effective-period
Device_0030de091099.SCHEDULE_0.exception-schedule
Device_0030de091099.SCHEDULE_0.weekly-schedule
when trying to write the exception schedule the diagviewer/wireshark reports an error:
'Device_0030de091099' Error writing value to object '04400000' property '00000026' array index '4294967295' failed with error class '2', error code '9'
To reproduce for example take the string from the exception schedule
{<0> {<1> {[10] 255.255.01.255},{[10] 255.255.02.255}}},{<2> },{(3) 1},{<0> {(0) 255.255.255.255}},{<2> },{(3) 1},{<0> {(0) 255.255.255.255}},{<2> {[11] 00:00:00:000},{[0]},{[11] 00:00:00:000},{[0]}},{(3) 1}
and change it to
03.255}}},{<2> },{(3) 1},{<0> {(0) 255.255.255.255}},{<2> },{(3) 1},{<0> {(0) 255.255.255.255}},{<2> {[11] 00:00:00:000},{[0]},{[11] 00:00:00:000},{[0]}},{(3) 1}
which still should be valid.
The weekly schedule also can't be written.
E.g. a string like this:
{<0> {[11] 08:00:00:000},{[2] 3},{[11] 18:00:00:000},{[2] 2}}
The effective period can be written
and change it to
The problem was addressed in the parsing of nested constructed types.
Issue Number: 34768
Fixed on Date: 7.7.2015
Versions: 7.20 0 BUILD 21629