IEC61850 and Process Gateway IEC870Slave Direct Command Execution with Interlock check
Hi,
I have a Zenon Energy Edition communicating to x IED's in IEC61850. A dispatch center is connected to the Zenon using the process gateway IEC870Slave.
I have a question about commands sent from a dispatch center without using the Select Before Operate function but with check of interlock conditions in Zenon and in the IED.
- If I deactivate "Select routing" in the process gateway, then the command is not passed through the Command Processing module. So I cannot check interlock equations in Zenon and I cannot set the QoC to check the interlock conditions in the IED.
- If I activate "Select routing", but I deactivate "Select before operate" on the command variable, the same happens. The Command Processing modules are bypasses, so the interlock conditions in Zenon are not checked. Also, the Qoc is not set because of this and all interlocks in the IED are bypassed as well.
Is there a way to send commands without using SBO at the dispatch center (Direct Execute is requested by the grid operator) but with checking interlock conditions in Zenon and in the IED?
Philippe
This is a migrated post! Originally posted on 24.08.2021 by user PhilippeVDT. Please be aware that information can be outdated.
Disclaimer
This document governs the use of our Community Forum. By registering and using the platform, you accept these conditions.
The COPA-DATA Community Forum serves to encourage the exchange of information and experience about the zenon software between forum users respectively zenon users.
Please mind that any published information on the Community Forum is the subjective opinion and view based on the experience and the level of knowledge of the author. COPA-DATA does not overtake any responsibility for the content and the accuracy of the shared information.
Users of the Community Forum are encouraged to share only well-founded experiences and to point out any risks associated with the implementation of proposed solutions to problems. COPA-DATA at its absolute discretion, reserves the right to moderate the forum. In this connection COPA-DATA may remove any information containing false facts, potentially dangerous solutions, bad language or content that may insult, degrade or discriminate others. COPA-DATA may block a non-complying user from forum access if the user violated this provision.
COPA-DATA reserves the right to change this document from time to time at own discretion.
Ing. Punzenberger COPA-DATA GmbH
Karolingerstraße 7b · 5020 Salzburg · Austria
www.copadata.com